Heat Loss from a Variable Frequency Drive

An amount of the power transferred through a variable frequency drive to the motor is lost as heat. The heat loss from a drive can be expressed as

Hloss = Pt (1 -ηd)         (1)

where

Hloss = heat loss to the variable-frequency drive surroundings (kW)

Pt = electrical power through the variable-frequency drive (kW)

ηd = variable-frequency drive efficiency

The heat loss expressed in imperial units

Hloss = Pt 3412 (1 -ηd)         (1b)

where

Hloss = heat loss to the variable-frequency drive surroundings (btu/h)

Pt = power in to the frequency drive (kW)

ηd = variable-frequency drive efficiency

To calculate maximum heat loss - the maximum power transmission through the variable-frequency drive must be used.

It is common that the heat loss from a frequency drive is in the range 2 - 6% of the KVA rating.

Necessary Ventilation for Cooling a Variable-Frequency Drive

Maximum ambient temperature for a frequency-drive is approximately 40oC (104oF). Since frequency-drives often are physical protected in small cabinets or small rooms, ventilation - or even cooling - may be needed to avoid overheating.

The mass flow of air needed for transporting heat from the variable-frequency drive can be expressed as

mair = Hloss / cp (tout - tin)         (2)

where

mair = mass flow of air (kg/s)

Hloss = heat loss to the frequency-drive surroundings (W)

cp = specific heat of air (kJ/kg oC) (1.005 kJ/kg oC standard air)

tout = temperature of air out (oC)

tin = temperature of air in (oC)

Combined with (1), the mass flow (2) can be expressed as:

mair =Pt (1 -ηd) / cp (tout - tin)         (2b)

The volume flow can be calculated by multiplying (2b) with the specific volume or inverted density:

qair = (1 / ρair) Pt (1 - ηd) / cp (tout - tin)         (2c)

where

ρair = density of air at the actual temperature (1.205 kg/m3 standard air)

Variable Frequency Drive - Heat Loss Air Cooling Chart

Variable frequency drive - power heat loss and required air cooling chart

Download and print Variable Frequency Drive Heat Loss Air Cooling Chart

Example - Ventilation and Cooling of a Variable-Frequency Drive

The heat generation by the variable frequency drive with maximum power of 100 kW and efficiency of 0.95,can be calculate with eq. 1 as

Hloss = (50 kW) (1 -95 / 100) 

      = 2.5 kW 

The mass of cooling cooling air through the cabinet when the maximum ambient operating temperature for the frequency drive is 40 oC and outside temperature of the cabinet is 20 oC can be calculated with eq. 2 as

mair = (2.5 kW) / (1.005 kJ/kg oC) ((40 oC) - (20 oC)) 

      = 0.125 kg/s   

The volume and density of air depends on the temperature of the air. The density of air at 20oC is 1.205 kg/m3 and 1.127 kg/m3 at 40 oC.

The volume flow at the inlet (20 oC):

qair = (1 / (1.205 kg/m3)) (0.125 kg/s)

    = 0.104 m3/s

    = 375 m3/h

The volume flow at the outlet (40 oC):

qair = (1 / (1.127 kg/m3)) (0.125 kg/s)

    = 0.111 m3/s

    = 400 m3/h

Related Topics

  • Miscellaneous

    Engineering related topics like Beaufort Wind Scale, CE-marking, drawing standards and more.

Related Documents

Search

Search is the most efficient way to navigate the Engineering ToolBox.

Engineering ToolBox - SketchUp Extension - Online 3D modeling!

3D Engineering ToolBox Extension to SketchUp - add parametric components to your SketchUp model

Add standard and customized parametric components - like flange beams, lumbers, piping, stairs and more - to your Sketchup model with the Engineering ToolBox - SketchUp Extension - enabled for use with older versions of the amazing SketchUp Make and the newer "up to date" SketchUp Pro . Add the Engineering ToolBox extension to your SketchUp Make/Pro from the Extension Warehouse !

Translate this Page

Translate this page to Your Own Language .

About the Engineering ToolBox!

Privacy Policy

We don't collect information from our users. More about

We use a third-party to provide monetization technologies for our site. You can review their privacy and cookie policy here.

You can change your privacy settings by clicking the following button: .

Citation

This page can be cited as

  • The Engineering ToolBox (2004). Variable Frequency Drives - Heat Loss and Required Air Cooling. [online] Available at: https://www.engineeringtoolbox.com/variable-frequency-drives-d_656.html [Accessed Day Month Year].

Modify the access date according your visit.

3D Engineering ToolBox - draw and model technical applications! 2D Engineering ToolBox - create and share online diagram drawing templates! Engineering ToolBox Apps - mobile online and offline engineering applications!

Unit Converter

















































5.8.12

.