Air - Specific Heat vs. Temperature at Constant Pressure
Online calculator with figures and tables showing specific heat (Cp and Cv) of dry air vs. temperature and pressure. SI and imperial units.
Specific heat (C) is the amount of heat required to change the temperature of a mass unit of a substance by one degree.
- Isobaric specific heat (Cp ) is used for air in a constant pressure (ΔP = 0) system.
- I sochoric specific heat (Cv ) is used for air in a constant-volume (isovolumetric or isometric) closed system.
Note! At normal atmospheric pressure of 1.013 bar - the specific heat of dry air - C P and CV - will vary with temperature. This may influence on the accuracy of air conditioning and industrial air handling process calculations. When calculating mass and volume flow of air in heated or cooled systems with high accuracy - the specific heat (= heat capacity) should be corrected according values in the figures and table below, or found by use of the calculator.
- For ordinary calculations - a value of specific heat cp = 1.0 kJ/kg K (equal to kJ/kg oC) or 0.24 Btu(IT)/lb °F - is normally accurate enough
- For higher accuracy - a value of Cp = 1.006 kJ/kg K (equal to kJ/kg oC) or 0.2403 Btu(IT)/lb °F - is better
Online Air Specific Heat Calculator
The calculator below can be used to estimate the specific heat of air at constant volum or constant pressure and at given temperature and pressure.
The output heat capacity is given as kJ/(kmol*K), kJ/(kg*K), kWh/(kg*K), kcal/(kg*K), Btu(IT)/(mol*°R) and Btu(IT)/(lbm *°R)
See also other properties of Air at varying temperature and pressure: Density and specific weight at varying temperature , Density at varying pressure , Diffusion Coefficients for Gases in Air , Prandtl Number , Specific heat at varying pressure , Thermal Conductivity , Thermal Diffusivity , Properties at gas-liquid equilibrium conditions and Air thermophysical properties at standard conditions and Composition and molecular weight ,
as well as Specific heat of Ammonia , Butane , Carbon dioxide , Carbon monoxide , Ethane , Ethanol , Ethylene , Hydrogen , Methane , Methanol , Nitrogen , Oxygen , Propane and Water .
Specific heat of air at 1 bar (0.1 mPa, 14.5 psi):
For full table with Isobaric heat capacity - rotate the screen!
Temperature | Isochoric specific heat (Cv) | Isobaric specific heat (Cp) | Cp/Cv | ||||||||||
[K] | [°C] | [°F] | [kJ/mol K] | [kJ/kg K] | [kWh/(kg K)] |
[kcal(IT)/(kg K)] |
[kcal(IT)/(lb °F)] | [kJ/mol K] | [kJ/kg K] | [(kW h)/(kg K)] | [kcal(IT)/(kg K)] [Btu(IT)/lb °F] |
[kcal(IT)/(lb °F)] | [-] |
60 | -213 | -352 | 0.03398 | 1.173 | 0.0003258 | 0.2802 | 0.2287 | 0.05506 | 1.901 | 0.000528 | 0.45405 | 0.37071 | 1.621 |
78.79 | -194 | -318 | 0.03044 | 1.051 | 0.0002919 | 0.2510 | 0.2050 | 0.05599 | 1.933 | 0.000537 | 0.46169 | 0.37695 | 1.839 |
81.61 | -192 | -313 | 0.02172 | 0.7500 | 0.0002083 | 0.1791 | 0.1463 | 0.03154 | 1.089 | 0.000303 | 0.26010 | 0.21237 | 1.452 |
100 | -173 | -280 | 0.02109 | 0.7280 | 0.0002022 | 0.1739 | 0.1420 | 0.03012 | 1.040 | 0.000289 | 0.24833 | 0.20276 | 1.428 |
120 | -153 | -244 | 0.02093 | 0.7225 | 0.0002007 | 0.1726 | 0.1406 | 0.02953 | 1.022 | 0.000283 | 0.24350 | 0.19930 | 1.415 |
140 | -133 | -208 | 0.02081 | 0.7184 | 0.0001996 | 0.1716 | 0.1401 | 0.02937 | 1.014 | 0.000282 | 0.24219 | 0.19774 | 1.411 |
160 | -113 | -172 | 0.02077 | 0.7172 | 0.0001992 | 0.1713 | 0.1399 | 0.02928 | 1.011 | 0.000281 | 0.24147 | 0.19716 | 1.410 |
180 | -93.2 | -136 | 0.02076 | 0.7166 | 0.0001991 | 0.1712 | 0.1397 | 0.02920 | 1.008 | 0.000280 | 0.24076 | 0.19657 | 1.407 |
200 | -73.2 | -99.7 | 0.02075 | 0.7163 | 0.0001990 | 0.1711 | 0.1397 | 0.02917 | 1.007 | 0.000280 | 0.24052 | 0.19638 | 1.406 |
220 | -53.2 | -63.7 | 0.02075 | 0.7163 | 0.0001990 | 0.1711 | 0.1397 | 0.02914 | 1.006 | 0.000279 | 0.24028 | 0.19618 | 1.404 |
240 | -33.2 | -27.7 | 0.02075 | 0.7164 | 0.0001990 | 0.1711 | 0.1397 | 0.02914 | 1.006 | 0.000279 | 0.24028 | 0.19618 | 1.404 |
260 | -13.2 | 8.3 | 0.02076 | 0.7168 | 0.0001991 | 0.1712 | 0.1398 | 0.02914 | 1.006 | 0.000279 | 0.24028 | 0.19618 | 1.403 |
273.2 | 0.0 | 32.0 | 0.02077 | 0.7171 | 0.0001992 | 0.1713 | 0.1398 | 0.02914 | 1.006 | 0.000279 | 0.24028 | 0.19618 | 1.403 |
280 | 6.9 | 44.3 | 0.02078 | 0.7173 | 0.0001993 | 0.1713 | 0.1399 | 0.02914 | 1.006 | 0.000279 | 0.24028 | 0.19618 | 1.402 |
288.7 | 15.6 | 60.0 | 0.02078 | 0.7175 | 0.0001993 | 0.1714 | 0.1399 | 0.02914 | 1.006 | 0.000279 | 0.24030 | 0.19620 | 1.402 |
300 | 26.9 | 80.3 | 0.02080 | 0.7180 | 0.0001994 | 0.1715 | 0.1400 | 0.02915 | 1.006 | 0.000280 | 0.24036 | 0.19625 | 1.402 |
320 | 46.9 | 116 | 0.02083 | 0.7192 | 0.0001998 | 0.1718 | 0.1403 | 0.02917 | 1.007 | 0.000280 | 0.24052 | 0.19638 | 1.400 |
340 | 66.9 | 152 | 0.02087 | 0.7206 | 0.0002002 | 0.1721 | 0.1405 | 0.02923 | 1.009 | 0.000280 | 0.24100 | 0.19677 | 1.400 |
360 | 86.9 | 188 | 0.02092 | 0.7223 | 0.0002006 | 0.1725 | 0.1409 | 0.02926 | 1.010 | 0.000281 | 0.24123 | 0.19696 | 1.398 |
380 | 107 | 224 | 0.02098 | 0.7243 | 0.0002012 | 0.1730 | 0.1412 | 0.02931 | 1.012 | 0.000281 | 0.24171 | 0.19735 | 1.397 |
400 | 127 | 260 | 0.02105 | 0.7266 | 0.0002018 | 0.1735 | 0.1417 | 0.02937 | 1.014 | 0.000282 | 0.24219 | 0.19774 | 1.396 |
500 | 227 | 440 | 0.02150 | 0.7424 | 0.0002062 | 0.1773 | 0.1448 | 0.02983 | 1.030 | 0.000286 | 0.24597 | 0.20083 | 1.387 |
600 | 327 | 620 | 0.02213 | 0.7641 | 0.0002123 | 0.1825 | 0.1490 | 0.03044 | 1.051 | 0.000292 | 0.25103 | 0.20496 | 1.375 |
700 | 427 | 800 | 0.02282 | 0.7877 | 0.0002188 | 0.1881 | 0.1536 | 0.03114 | 1.075 | 0.000299 | 0.25675 | 0.20963 | 1.365 |
800 | 527 | 980 | 0.02351 | 0.8117 | 0.0002255 | 0.1939 | 0.1583 | 0.03183 | 1.099 | 0.000305 | 0.26249 | 0.21432 | 1.354 |
900 | 627 | 1160 | 0.02415 | 0.8338 | 0.0002316 | 0.1991 | 0.1626 | 0.03247 | 1.121 | 0.000311 | 0.26772 | 0.21858 | 1.344 |
1100 | 827 | 1520 | 0.02525 | 0.8716 | 0.0002421 | 0.2082 | 0.1700 | 0.03356 | 1.159 | 0.000322 | 0.27675 | 0.22596 | 1.329 |
1500 | 1227 | 2240 | 0.02673 | 0.9230 | 0.0002564 | 0.2204 | 0.1800 | 0.03505 | 1.210 | 0.000336 | 0.28901 | 0.23597 | 1.311 |
1900 | 1627 | 2960 | 0.02762 | 0.9535 | 0.0002649 | 0.2277 | 0.1859 | 0.03593 | 1.241 | 0.000345 | 0.29631 | 0.24193 | 1.301 |
Unit conversion:
british thermal unit(International table) = [Btu(IT)], degree celcius = [°C], degree fahrenheit = [°F], kelvin = [K], degree rankin = [°R], joule = [J], kilocalorie(International table) = [kcal(IT)], kilogram = [kg], kilojoule = [kJ], kilowatthour = [kWh], mole = [mol], pound =[lb]
K in the units can be replaced by °C, and vise versa. °R in the units can be replaced by °F, and vise versa.
- 1 Btu/(lb °F) = 1 Btu/(lb °R) = 1 kcal(IT)/(kg °C) = 1 kcal(IT)/(kg K) = 4186.8 J/(kg K) = 0.81647 kcal(IT)/(lb °F) = 1.163x10-3 kWh/(kg K)
- 1 J/(kg K) = 1 J/(kg °C) = 2.3885x10-4 kcal(IT)/(kg oC) = 2.3885x10-4 Btu/(lb °F) = 1.9501x10-4 kcal(IT)/(lb °F)
- 1 kcal(IT)/(kg °C) = 1 Btu/(lb °F) = 4186.8 J/(kg K) = 0.81647 kcal(IT)/(lb °F) = 1.163x10-3 kWh/(kg K)
- 1 kcal(IT)/(lb °F) = 1.2248 Btu/(lb °F) = 1.2248 kcal(IT)/(kg °C) = 5127.9 J/(kg K)
- 1 kJ/(kg K) = 1 kJ/(kg °C) = 1000 J/(kg K) = 1000 J/(kg °C) = 0.23885 kcal(IT)/(kg °C) = 0.23885 Btu/(lb °F) = 0.19501 kcal(IT)/(lb °F) = 2.7778x10-4 kWh/(kg K)
- 1 kWh/(kg K) = 0.85985 kcal(IT)/(kg °C) = 0.85985 Btu/(lb °F) = 3.6 kJ/(kg K)
- 1 mol of air = 28.96546 g
Air Psychrometrics
Moist and humid air calculations. Psychrometric charts and Mollier diagrams. Air-condition systems temperatures, absolute and relative humidities and moisture content in air. -
Fluid Mechanics
Gases and Compressed Air
Properties of air, LNG, LPG and other common gases. Pipeline capacities and sizing of relief valves. -
Material Properties
Dry air is a mechanical mixture of nitrogen, oxygen, argon and several other gases in minor amounts. -
Air - Density vs. Pressure and Temperatures
Air density at pressure ranging 1 to 10 000 bara (14.5 - 145000 psi) and constant selected temperatures. -
Online calculator, figures and tables showing density, specific weight and thermal expansion coefficients of air at temperatures ranging -100 to 1600 °C (-140 to 2900 °F) at atmospheric and higher pressure - Imperial and SI Units. -
Diffusion coefficients (D12) for gases in large excess of air at temperatures ranging 0 - 400 °C. -
Air - Dynamic and Kinematic Viscosity
Online calculator, figures and tables with dynamic (absolute) and kinematic viscosity for air at temperatures ranging -100 to 1600°C (-150 to 2900°F) and at pressures ranging 1 to 10 000 bara (14.5 - 145000 psia) - SI and Imperial Units. -
Dry air is a mixture of gases where the average molecular weight (or molar mass) can be calculated by adding the weight of each component. -
Air - Prandtl Number
Prandtl number for air vs. temperature and pressure. -
Properties of air change along the boiling and condensation curves (temperature and pressure between triple point and critical point conditions). An air phase diagram included. -
Air - Specific Heat Ratio
Specific Heat Ratio of air at temperatures ranging -40 - 1000 degC (-40 - 1500 degF) at standard atmospheric pressure - Imperial and SI Units. -
Figures and tables with isobaric (Cp) and isochoric (Cv) specific heat of air at constant temperature and pressure ranging 0.01 to 10000 bara. -
Figures and tables withdry air thermal diffusivity vs. temperarure and pressure. SI and Imperial units. -
Thermal properties of air at different temperatures - density, viscosity, critical temperature and pressure, triple point, enthalpi and entropi, thermal conductivity and diffusivity and more. -
Online calculators, figures and tables showing specific heat, Cp and Cv, of gasous and liquid butane, C4H10, at varying temperarure and pressure, SI and Imperial units. -
Dry Air - Thermodynamic and Physical Properties
Thermodynamic properties of dry air - specific heat, ratio of specific heats, dynamic viscosity, thermal conductivity, Prandtl number, density and kinematic viscosity at temperatures ranging 175 - 1900 K. -
Online calculators, figures and tables showing specific heat , Cp and Cv, of gasous and liquid ethanol at temperatures ranging from -25 to 325 °C (-10 to 620 °F) at atmospheric and higher pressure - Imperial and SI Units. -
Gases - Specific Heats and Individual Gas Constants
Specific heat at constant volume, specific heat at constant pressure, specific heat ratio and individual gas constant - R - common gases as argon, air, ether, nitrogen and many more. -
Humid Air - Heating
Enthalpy change and temperature rise when heating humid air without adding moisture. -
Moist Air - Enthalpy
Sensible and latent heat of moist air. -
Removing Heat with Air
Calculating heat removed with air by measuring the wet bulb temperature. -